Hi. 

So today i noticed my light was out. 

This is 1 600 watt bulb on a magnetic ballast and a 4 inch extrecator fan hooked up with ducting. Nothing else runs on this outlet.

Check out the pictures. Id like to know why this happened. Im not sure if it started in the timer or the outlet. It also damaged the power cord running to the power strip. The breaker didnt trip(20 amp breaker) ive been running this outlet for 8 years with no problem, sometimes ill run 2 600watters on it.

20170906_115806.jpg

Link to comment
Share on other sites

That's where it always happens, right at the plug. Plant lights, Christmas lights, any appliance that draws a lot and gets plugged in a lot. The weight of a heavy cord, the weight of a timer. Over time the connection will fail, and when it does you get arcing and melted plastic. Set up your plugs in a way so that when this happens it just burns up the plastic and nothing else can catch fire. That is exactly why plugs are in metal boxes. This stuff happens. I've had it happen on my Christmas lights, on air conditioner plugs, on my plant light extension cord, and once on a timer. 

Do your best to have all of your plugs getting a nice tight connection and keep flammable items away from plugs. That's the answer to this problem. 

Link to comment
Share on other sites

Follow up;

Nice pictures. Makes it really easy to see exactly what happened. You can see by how the plug receptacle is melted that the one prong on the timer wasn't getting a good connection and it arced and sparked and burned. Even perfect home wiring with brand new circuit breakers will not help in a situation like that. 

Link to comment
Share on other sites

1 minute ago, zapatosunidos said:

For some reason I thought 10 gauge was required on 20 amp circuits, but maybe that is just with a run of a certain length from the panel.

It would have to be a long distance from panel to use 10g. 

Some houses are built with 12/2 and 20 amp circuits. Cost is more for materials and wiring is harder to work with.

Link to comment
Share on other sites

We ran dedicated plugs and wiring to a stand alone  power box in the flower room  with breakers also went with 220 over 110 to lessen the amps on the wiring and box  just in case I also have  tank extinguishers in each grow area  to give me peace of mind while I am out on the road away from home.

Link to comment
Share on other sites

I had a 220 intermatic timer melt on me. i think it arc'd due to bad/lose connection on the plug, possibly because of corrosion on the hottub plug.

 

good reason to follow the recommended rules of grow rooms. glad you didnt lose anything important!

 

do we have a list of tips? theres some in some grow books.

count your amps.

do not use any wires with cuts or nicks in them.

touch wires after they are on for a time to see if they get hot.

keep wires and cables tied and above the ground if possible.

do not run extension cords over carpet.

keep fire extinguishers up to date and handy.

check smoke detectors on a regular basis.

Link to comment
Share on other sites

5 minutes ago, matt79 said:

I looked closer at the wire coming out of the fuse box. All 20amp breakers on #14 wire for every circuit in the house. Thats no good. Im gonna go through and change all the breakers to 15amps.

My garage grow room i used all 12gauge wire with a dedicated 100amp sub panel so no worries there

Yup. That's a code violation.

Link to comment
Share on other sites

8 hours ago, matt79 said:

I looked closer at the wire coming out of the fuse box. All 20amp breakers on #14 wire for every circuit in the house. Thats no good. Im gonna go through and change all the breakers to 15amps.

My garage grow room i used all 12gauge wire with a dedicated 100amp sub panel so no worries there

Your kitchen and laundry could be #12

Link to comment
Share on other sites

  • 2 months later...

The timer is only rated for 1000 watts tungsten load. You can only operate at 80%. Which means the timer is good for 800 watts total continuous.

Two 600 watt ballast at times like you said is an overload for the timer.

Looks like a Pass & Seymour receptacle. Were the wires connected at the screw or pushed into the back of the receptacle?

I use the Intermatic T1004R timer in a majority of the grows I wire.

I have equipment on these timers for over 40 years with no problems.

 

Link to comment
Share on other sites

Back when I first started I had similar experiences.  In working with an electrician he rec'c I use all 20 amp heavy duty duplex outlets regardless of any assumptions about lower loads.  Only cost a few dollars more per outlet, but cheap peace of mind.   He pointed out that the cheap ones 15 amp ones that you find in the bins at HD have only one spring loaded contact that grabs the prong on the plug where as the better outlets have two spring loaded contacts, i.e. less likely to loose contact over time.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...